Код: Выделить всё
test board 1a14 Please Wait
TEST RESULTS
Port Mtce Name Alt. Name Test No. Result Error Code
01A14 CLSFY-BD 52 PASS
01A1401 ETR-PT 42 FAIL 110
01A1401 ETR-PT 43 PASS
01A1402 ETR-PT 42 FAIL 110
Код: Выделить всё
110-122
130
FAIL A Tone Level Test failed.
Forward/backward MFC signals not correctly generated/detected.
1. Run the short test sequence with test port location
2. If the problem persists, the system is still operating properly but
capacity will be reduced. To restore performance to normal,
replace the circuit pack containing the defective port. See
TONE-BD (Tone-Clock Circuit Pack) for the procedures to
replace a Tone-Clock circuit pack.
test tone-clock 1a проходит на ура. 01A TN2312BP hw12fw51
Код: Выделить всё
status port-network 1
PORT NETWORK STATUS
Major Minor Warning Carrier PN Control Internet Protocol (IP)
PN Alarms Alarms Alarms Locs Active Standby Connected Port Network
1 0 8 23 01A up
01B
TDM Service Control Dedicated TONE/ Service System System
Bus State Channel Tones CLOCK State Clock Tones
A in y n 01A in active active
B in n y
Service Major Minor Bus Open Bus
PKT State Alarms Alarms Faults Leads
1 in n n 0 0
Код: Выделить всё
The TN2314 Processor and TN744E Call Classifier and Tone Detector circuit
packs, needed for the S8100 model, are not used and must be removed if the
G600 is being migrated from an S8100 Media Server. All gateways are port
gateways, though the bottom gateway (serving as control cabinet A) contains the
IPSI circuit pack.